Does the 2008 code require 1/2 conduit to be supported every 10 feet?
H harleyandgun Member Dec 4, 2009 #1 Does the 2008 code require 1/2 conduit to be supported every 10 feet?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Dec 4, 2009 #2 Every 10 ft and with 3 ft of any j box, conduit body, etc. There may be some exceptions such as 300.12
Every 10 ft and with 3 ft of any j box, conduit body, etc. There may be some exceptions such as 300.12
iwire Moderator Staff member Location Massachusetts Dec 5, 2009 #3 harleyandgun said: Does the 2008 code require 1/2 conduit to be supported every 10 feet? Click to expand... Assuming RMC / IMC I agree with Gus, if it happens to be PVC conduit it must be supported every three feet.
harleyandgun said: Does the 2008 code require 1/2 conduit to be supported every 10 feet? Click to expand... Assuming RMC / IMC I agree with Gus, if it happens to be PVC conduit it must be supported every three feet.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Dec 5, 2009 #4 Thanks , Bob. My eyes read "emt" into the,question... old age.,.... View attachment 4063