Conduit supports for tee fitting
Isaiah
Baton Rouge
Electrical Inspector
If I have a TEE condulet with trade size conduit (equal to condulet) entries - do I still need supports within 3 feet on all three sides of the TEE?
Enviado desde mi iPhone utilizando Tapatalk
Rigid, IMC or PVC no you dont. PVC its 352.10(I) in my 2023 book.
EMT yes at least the way 350.30(A) reads in my 2023 book I'd say yes.
As pipe bender stated you're limited by the raceway type as to when the raceway can support the conduit body without additional support.
314.23(E) Raceway-Supported Enclosure, Without Devices, Luminaires, or Lampholders.
An enclosure that does not contain a device(s), other than splicing devices, or supports a luminaire(s), a lampholder, or other equipment and is supported by entering raceways shall not exceed 1650 cm3 (100 in.3) in size. It shall have threaded entries or identified hubs. It shall be supported by two or more conduits threaded wrenchtight into the enclosure or hubs. Each conduit shall be secured within 900 mm (3 ft) of the enclosure, or within 450 mm (18 in.) of the enclosure if all conduit entries are on the same side.
Exception: The following wiring methods shall be permitted to support a conduit body of any size, including a conduit body constructed with only one conduit entry, provided that the trade size of the conduit body
is not larger than the largest trade size of the conduit or tubing:
(1) Intermediate metal conduit, Type IMC
(2) Rigid metal conduit, Type RMC
(3) Rigid polyvinyl chloride conduit, Type PVC
(4)Reinforced thermosetting resin conduit, Type RTRC
(5)Electrical metallic tubing, Type EMT
Let’s say I have 1” RGS run and the Tee condulet is supported on one side within 3 feet (roughly) - of the Tee…
Where then would I need supports for the other two sides if all conduit entries are 1”?
I’m assuming it would be 10 feet from the 1st support?
This has been debated here before but the way that I read it is that when the conduit body is the same size you just ignore it when supporting the raceway. If you had one support at 3' from the conduit body the next support can be 7' from the first support.
That’s the way I read it also. Thanks for confirming