ed downey

Senior Member
Location
Missouri
There is box that is mounted about 8' below a ceiling in a warehouse. The box is suppoted by 3/8" allthread rod to the structure above at each corner. The 1 1/2" EMT that terminates in the 12"x12"x6" junction box is only supported at the ceiling level. Does this conduit need an intermediate support between the ciling and the junction box.

Thanks for any help.
-Ed Downey
 
Re: Conduit Supports

358.30(A) requires a support within 3' of the box or use the exception no. 1 to 358.30(A) and you can be 5' from the box.
 