wrobotronic
Senior Member
- Location
- Colorado
Hello All,
i have a situation where a contractor is telling me to free air conductors that are feeding a huge generator. The main run is PVC from the ATS and pops up inside the generator enclosure. Then flex from there to the OCPD cabinet.
basically, the UG 3 1/2” pvc needs to transition to 3 1/2” flex to get in the bottom of cabinet.
He wants me to cut off the PVC at the ground and eliminate the flex, thus free air about 2 to 3 feet.
I was was under the impression that the raceway needs to be completed from start to finish.
While he says it’s allowed because the inside of the generator is only accessible by authorized personnel.
is there a code section requiring the conduit run to terminate/ be completed. Or is he right (if so is there an article that covers his method)?
i have a situation where a contractor is telling me to free air conductors that are feeding a huge generator. The main run is PVC from the ATS and pops up inside the generator enclosure. Then flex from there to the OCPD cabinet.
basically, the UG 3 1/2” pvc needs to transition to 3 1/2” flex to get in the bottom of cabinet.
He wants me to cut off the PVC at the ground and eliminate the flex, thus free air about 2 to 3 feet.
I was was under the impression that the raceway needs to be completed from start to finish.
While he says it’s allowed because the inside of the generator is only accessible by authorized personnel.
is there a code section requiring the conduit run to terminate/ be completed. Or is he right (if so is there an article that covers his method)?