conduit to flex

Status
Not open for further replies.

ktollar

Member
Will ridgid conduit to a rigid coupling to seal tight connector meet nec 300-15 (F)? Is a box required?
 

Johnmcca

Senior Member
I'd say no box required. As long as all your fittings are listed and there is no splicing of the conductors. At least I've never been called on it. How else do you make motor connections?
 

Smart $

Esteemed Member
Location
Ohio
ktollar said:
Will ridgid conduit to a rigid coupling to seal tight connector meet nec 300-15 (F)? Is a box required?
The issue you present has been debated. Most recently in:

http://www.mikeholt.com/code_forum/showthread.php?t=81787

It has been done the way you mention seemingly forever, and I have never heard of such application being rejected by an AHJ. However, an alternative is to use connectors such as T&B's 5271 series with female NPT hub...
tc_1_g_5271series_0_ph.jpg
 