TwinCounty

New member
Location
USA
I am considering wiring a subpanel to a second floor in a residential structure.

The feed will be PVC40 conduit on the exterior into the attic, across the attic and down into an interior wall on the second floor.

I'm thinking a 100 or 125 amp, there. Considering a 2-3w/G romex, into a 2in conduit (with bends), and then clamped across the attic, and then down to the panel. This run is around 55 feet (20 up outside, 30 over in attic, and 5 down the wall)

Questions:
1. Can/should I use THHN, and if so, must i also run the conduit through the attic and down the wall. Thinking this because of wire temp rating/derating.
1a. If I use THHN, or other type cable, #2 or #3?
2. Can I use aluminum, either as the 2-3 or the THHN of some size?
3. My review is that voltage drop would be <3 percent. Any thoughts?

Instead of running to the attic, I could run under the elevated house, and then up an interior wall, to the joist space on the ceiling, a couple of feet there, and then up the second story wall to the subpanel. Do I need to place THHN in a conduit under the house, or in the walls/ceiliings? Does it need to be protected?

Elevated houses are raised on piers, 3 feet above the ground, and the underside of the floor joists are exposed.

Finally, another question: running a 60amp 6-3 feed to a detached garage, I suspect I need to use wet location to go the 20 feet underground in a PVC conduit. 18 inches down....? A single run from the main panel would be.....UF? USE-2? I figured on clamping under the house, and then joining the conduit at the rear, and not placing conduit all through underneath. Cu vs Al ? Better/easier/harder to use NM-B from the panel back, and then use USE in the conduit with a junction box?
 
I am closing this thread, in accordance with the Forum rules. This Forum is intended to assist professional electricians, inspectors, engineers, and other members of the electrical industry in the performance of their job-related tasks. However, if you are not an electrician or an electrical contractor, then we are not permitted to help you perform your own electrical installation work.


If I have misjudged the situation, if for example this project is related to your work, then send me a Private Message. If you can show me that I am wrong, and that you are a licensed electrician (or at least a licensed apprentice), then I will reopen your post, and offer an apology for the delay and inconvenience.

A reminder to all members, if you see a questionable post, feel free to report it by clicking the
report-40b.png
button at the bottom left corner of the post.
 
Status
Not open for further replies.
Top