Can a single conduit share branch circuits that are derived from separate services? For example; there is a service set for exterior lighting and branch circuits serving those lights. A second service set up in a location with branch circuits serving various receptacle locations outside. Their branch circuits share the same conduit for some underground runs and same pull box in various locations.
By definition, only the Branch circuit conductors, 1000V or less, will be sharing the same conduit, but they are from separate services and the main service disconnects are not located within sight of each other.
300.3(C) says" Conductors of different systems", which would seem to permit it, but I do not believe that's the correct section, but the closest I could find.
By definition, only the Branch circuit conductors, 1000V or less, will be sharing the same conduit, but they are from separate services and the main service disconnects are not located within sight of each other.
300.3(C) says" Conductors of different systems", which would seem to permit it, but I do not believe that's the correct section, but the closest I could find.