Do you mean the horixontal runs as well?Not required by NEC, but required by the drawing.
But these arent GEC's. This is a bunch of superfluous waste some grounding nutjob drew up who has no idea what he is doing.Enclosing a Grounding Electrode Conductor (GEC) in EMT or conduit is only required were the GEC is subject to physical damage. If metal conduit is used the GEC must be bonded to the metal conduit at both ends of the portion of the GEC that it protects.
Tom Horne
May I ask what brought you to the conclusion that the person who specified the bonding conductors shown in that print is "some grounding nutjob" rather than a communications engineer or a communications wireman...?But these aren't GECs. This is a bunch of superfluous waste some grounding nutjob drew up who has no idea what he is doing.
based on the fact that pretty much of what is shown there would already be bonded, the over the top wire sizes, and two decades of seeing over the top bonding and grounding done with pretty much zero justification for it with case studies or even basic electrical theory. IF it was drawn by a "communications engineer" (or any engineer in fact, some of them are the worst with grounding ridiculousness) I would be even MORE skeptical that it serves any purpose We dont know exactly what it is for, but it does not appear to be a cell site room IMO.May I ask what brought you to the conclusion that the person who specified the bonding conductors shown in that print is "some grounding nutjob" rather than a communications engineer or a communications wireman...?
Tom Horne