C chocho77 Member Nov 12, 2009 #1 Can anybody clarify what is the "Ambient temperature" when using Table 310.15 (B)(2)(c) for Seattle for example?
Can anybody clarify what is the "Ambient temperature" when using Table 310.15 (B)(2)(c) for Seattle for example?
H hardworkingstiff Senior Member Location Wilmington, NC Nov 12, 2009 #2 Maybe this can help? http://www.copper.org/applications/electrical/building/derating_table.html#WA
H hardworkingstiff Senior Member Location Wilmington, NC Nov 12, 2009 #4 chocho77 said: Thank you! Why there are two columns 12" Distance above roof? Click to expand... Typo, if you go up to the top of the page you will see the 1st column is listed as 1/2". That matches the distances in Table 310.15(B)(2)(c). Good catch!
chocho77 said: Thank you! Why there are two columns 12" Distance above roof? Click to expand... Typo, if you go up to the top of the page you will see the 1st column is listed as 1/2". That matches the distances in Table 310.15(B)(2)(c). Good catch!
W W6SJK Senior Member Nov 14, 2009 #6 Thanks for the link! I wrote the webmaster to report the error.