Conduits on ground in front of electrical panel working space

Status
Not open for further replies.

Johnhall30

Senior Member
Location
New Orleans, LA
Occupation
Engineer
Electrical panel is mounted on top of a flat roof section of a 5 story building. RMC conduit is running on top of the roof surface supported on dura-block 3-4 inches above the roof membrane. The conduits pass directly under and in front of the electrical panel and are technically within the working space of the panel.

This is a new construction project. Should there be a platform installed in front of the electrical panel, over the conduits, to make a cleaner working space?

Code opinions?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Yes, you need a platform. At a minimum you probably have a tripping hazard which might interest OSHA.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
IMO, without a platform it is subject to physical damage. Especially the way the conduits are installed next to each other.

I will guess the width of the installed conduits is about 16"?
 