Hi All,
I have some outdoor receptacles and I am routing the conduits below floor for slab-on-grade floor. We usually specify 3/4'' conduit as minimum, can you have 3 of 3/4'' conduits entering the bottom of a junction box? Typically 4'' SQ or 4-11/16'' SQ junction box has 3 knockouts on the sides, mostly 1/2'' knockouts, I did found junction box with 3 - 3/4'' knockouts on the sides: https://www.emerson.com/documents/c...sion-rings-covers-catalog-pages-en-724286.pdf
Wondering if you can have 3 - 3/4'' conduits entering one side of junction box and if the box is common. Also after adding the locknuts, bushing, connectors etc, if still can connect 3 - 3/4'' into one side of junction box.
Is it common to route receptacles in a room in a loop so each junction box has only one conduit in and one conduit out? or branch out from one junction box and feed two sides of the room, and that junction box will have one conduit in and two conduits out?
Thanks.
I have some outdoor receptacles and I am routing the conduits below floor for slab-on-grade floor. We usually specify 3/4'' conduit as minimum, can you have 3 of 3/4'' conduits entering the bottom of a junction box? Typically 4'' SQ or 4-11/16'' SQ junction box has 3 knockouts on the sides, mostly 1/2'' knockouts, I did found junction box with 3 - 3/4'' knockouts on the sides: https://www.emerson.com/documents/c...sion-rings-covers-catalog-pages-en-724286.pdf
Wondering if you can have 3 - 3/4'' conduits entering one side of junction box and if the box is common. Also after adding the locknuts, bushing, connectors etc, if still can connect 3 - 3/4'' into one side of junction box.
Is it common to route receptacles in a room in a loop so each junction box has only one conduit in and one conduit out? or branch out from one junction box and feed two sides of the room, and that junction box will have one conduit in and two conduits out?
Thanks.