Condulet C sizing 4" conduit

Status
Not open for further replies.

erbsnack

Member
Location
new york city
Is there a condulet c available that I can run 4 500 kcmil + 1 350 kcmil in? the standard ones I see are for 3 350 kcmil max.
looks like I would need a condulet C that's 32" long! Is that right? does that exist?

Thanks all.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes, it needs to meet the 8X rule for a straight pull to count as a pull point or the sizes and quantity printed on the conduit body may be used when less than 8X. Never seen one listed for what you're pulling so you'll probably need a pull box.
 