Ground wires are included in the fill calculations. .
That's confusing. How about:
From Chapter 9:
(3) Equipment grounding or bonding conductors, where installed, shall be included when calculating conduit or tubing fill. The actual dimensions of the equipment grounding or bonding conductor (insulated or bare) shall be used in the calculation.
I have an abandoned 1" emt conduit that I was hoping to use for a 100 amp single phase feeder. (3) #3 and a #8 ground thhn, but the 1" Lb's that are in place are only capable of handling (3) #4's. I believe the 1" Conduit is large enough but I would have to change out the (2) Lb's to 1 1/4" SLB's that have a capacity of 13.5 Cu. inches. Not sure if this will suffice or if I need to start from scratch. I can't use Full size LB's in this case.
Can't you use the EMT as the EGC?I have an abandoned 1" emt conduit that I was hoping to use for a 100 amp single phase feeder.
Can't you use the EMT as the EGC?