Suppose I have 3#1 phase conductors, 1#6G and 32#12 control wires (all wire rated 600V, for an industrial motor application) in a 3" conduit and an electrician has already installed a bunch of Form 8 LB condulets throughout the run which don't meet the 6x rule.
Per 314.28 (A)(3) Smaller Dimensions: the distance to the opposite wall rule for conduits containing #4 or larger does not have to be adhered to as long as the conduit body has been marked with maximum size of conductors permitted.
In my case, these condulets are stamped at 3#2/0, so my question is this: Are we compliant simply because the only wires in my condulet larger than #4 are the 3#1's which occupy less space than the 3#2/0's or do I somehow have to account for the 1#6 and 32#12's in conjunction in a different manner?
Thanks
Per 314.28 (A)(3) Smaller Dimensions: the distance to the opposite wall rule for conduits containing #4 or larger does not have to be adhered to as long as the conduit body has been marked with maximum size of conductors permitted.
In my case, these condulets are stamped at 3#2/0, so my question is this: Are we compliant simply because the only wires in my condulet larger than #4 are the 3#1's which occupy less space than the 3#2/0's or do I somehow have to account for the 1#6 and 32#12's in conjunction in a different manner?
Thanks