ConEd 480 or 460?

Merry Christmas

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
Is anyone familiar with ConEd requirements in lower New York? Do they provide 480V or 460V? We have a client who is having a lot of trouble with voltage dips causing issues on HVAC equipment because they have 460V coming into the building. The primary transformer says 480V/277, but that is not what we are reading.

I recently metered the system for a month, and there are a lot of fluctuations in the voltage. If anyone would like to see the results, feel free to ask. I am always happy to hear others opinions.
 

SceneryDriver

Senior Member
Location
NJ
Occupation
Electrical and Automation Designer
When we moved our shop two years ago, we discovered that the building we moved to had a service tapped for 460V. When the voltage would sag under heavy loads, our CNC machines would sometimes fault on low voltage. After much back and forth with PSE&G, they finally came out, did a full building shutdown at the pole, and changed the tap on the transformer. The paperwork took months. The actual work took less than 5 minutes.

Do you have a padmount transformer or pole pigs? The padmounts seem to be much easier for the POCO to retap and adjust.



Scenerydriver
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
When we moved our shop two years ago, we discovered that the building we moved to had a service tapped for 460V. When the voltage would sag under heavy loads, our CNC machines would sometimes fault on low voltage. After much back and forth with PSE&G, they finally came out, did a full building shutdown at the pole, and changed the tap on the transformer. The paperwork took months. The actual work took less than 5 minutes.

Do you have a padmount transformer or pole pigs? The padmounts seem to be much easier for the POCO to retap and adjust.



Scenerydriver
I actually had issues recently PSE&G with a 460V service. They wanted to charge the client $70k to change the transformer because it was from 1986 and didn't have a way to change the taps.

The client we have in Westchester has a padmount transformer. It even says 480/277 on the side., but that is not what they are getting.
 

SceneryDriver

Senior Member
Location
NJ
Occupation
Electrical and Automation Designer
I actually had issues recently PSE&G with a 460V service. They wanted to charge the client $70k to change the transformer because it was from 1986 and didn't have a way to change the taps.

The client we have in Westchester has a padmount transformer. It even says 480/277 on the side., but that is not what they are getting.
Our building's transformer had a built-in tap changer. Once they had the power off at the pole by pulling the cutouts, they just had to rotate a dial. It was like setting the cycle on your clothes dryer. I had no idea it could be that easy. I thought they'd be moving cables to different taps or something.

$70k is nuts! PSE&G always try to make it the customer's problem. The trick is getting someone with half a brain - the low level drones who answer the phone are not exactly empowered to help anyone with anything.