Conflict between UL and NEC?

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
300.11(A)(2)Exception: The ceiling support system shall be permitted to support branch-circuit wiring and associated equipment where installed in accordance with the ceiling system manufacturer?s instructions.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
WirenutGP said:
How can they be approved for that application and comply with NEC?

I know of no UL requirement that an item must comply with the NEC for it to be listed.

For example, there is a UL Listing for cord and plug connected condensate pumps, but article 408 prohibits them from being installed above drop ceilings.
 

WirenutGP

Member
The cord and plug connections can be used in different locations, the clips are made for just one. Now to track down suspended ceiling manufacturers' requirements.

Thanks
 

sandsnow

Senior Member
I looked up the link and found this:

This product is not currently available in the country you have selected. To view more information on this product, please change your country using the Change link above.

Looks like a non issue for us here in the states.
 