Now days with most water piping being entirely PEX (even the supply at the street), in a wood framed building there may only be grounding to the UFER. So do we only need to size the service ground wire #4 CU even if the service is 1000A, for example?
This example below has me a little confused, because it says the jumper from the busbar to the UFER is a GEC and needs to be sized per 250.66 using the sum of the circular mil of the largest ungrounded conductors. I would have thought the connection from the busbar to the UFER would only be required to be #4 CU per 250.66(B). So it got me thinking about cases where there only a UFER and no water or metal to bond to.
This example below has me a little confused, because it says the jumper from the busbar to the UFER is a GEC and needs to be sized per 250.66 using the sum of the circular mil of the largest ungrounded conductors. I would have thought the connection from the busbar to the UFER would only be required to be #4 CU per 250.66(B). So it got me thinking about cases where there only a UFER and no water or metal to bond to.