First, AIC means Amps Interrupting Current
When the utility company gives you this number, make sure you ask them exactly where on the system this number applies.
If it is on the LV side of a distribution transformer that feeds the residence then compare it to the AIC or KAIC rating of the main breaker and panelboard. If the number they give you is lower than the breaker and panel rating then your done. However, if the number they give you is higher, then you will need to calculate the value at the panelboard. The calculated value at the panelboard will be lower due to the impedance in the cable. If the calculated number is still higher than the panel rating, than you have a problem.