Confused by construction types

Status
Not open for further replies.

wesley_l

Member
Location
Sacramento
Occupation
Electrician
Hi. I’m starting a bid on a 5 story hotel, construction type 3a… construction type III, IV, V Nm-B is permitted. I’ve looked up what type construction 3a is, it says non-combustible walls but Wood floors and ceilings. I’ve looked at the plans and it seems the rooms are wood framed. Question, IS NM-B PERMITTED?
 
But if there is a meeting room with more than 100 person capacity that peticular room is a "place of assembly" so no NM in that rooms walls. This still allows you to wire in NM in the rest of the hotel.

Double check specs because hotels are usually national and if national there may be specs that they just don't want to show you that are referenced in the contract.
 
A lot of these types of facilities, at least the ones around here, have lay-in tile ceilings in the common areas. Just open structural members above the lay-in tiles.
Every hotel I've seen has a fire ceiling above or normal drywalled ceiling. Only big retail I've seen have direct framing members above drop ceiling
 