I am calculating max number of wires in conduits and came across this
From table 5 in chapter 9 THHN No.6 conductor area is 0.0507 in2
And from table 4 article 344 6?? RMC fill area at 40% is 11.663 in2
Now 11.633 / 0.0507 = 230.039 in2 give me the max number of wires in that raceway at or bellow 40%
But if I try to use table C.8(A) would show a different value of 258
What I am missing
Best regards
HP