Am I really off base or did the CMP not read the code section?
If this section only applies to conductors in raceways or cables, then what is the purpose of the words: "...or where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 600mm (24 in.) and are not installed in raceways ..."??
text in red = text to be deleted6-44 Log #3390 NEC-P06 Final Action: Reject
(310.15(B)(3)(a))
________________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Recommendation: Add new text to read as follows:
(3) Adjustment Factors.
(a) More Than Three Current-Carrying Conductors in a Raceway or Cable. Where the number of current-carrying conductors in a raceway or cable
exceeds three, or where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 600
mm (24 in.) and are not installed in raceways, the allowable ampacity of each conductor shall be reduced as shown in Table 310.15(B)(3)(a). Each current carrying conductor of a paralleled set of conductors shall be counted as a current-carrying conductor.
Substantiation: Delete ?in a Raceway or Cable?. Those words are in conflict with the wording in the section itself. The section wording makes it clear that a
current adjustment factor is required for three or more current carrying conductors that are installed without maintaining spacing and are not in a
raceway or cable.
Panel Meeting Action: Reject
Panel Statement: Section 310.15(B)(3)(a) is specific to conductors in raceway or cable. This section provides references to other sections, but contains rules for only conductors in raceways or cables.
Number Eligible to Vote: 10
Ballot Results: Affirmative: 10
If this section only applies to conductors in raceways or cables, then what is the purpose of the words: "...or where single conductors or multiconductor cables are installed without maintaining spacing for a continuous length longer than 600mm (24 in.) and are not installed in raceways ..."??