I'm looking at the label on this Siemens plug-on neutral load center: https://www.cityelectricsupply.com/...-225a-42-spaces-64-circuits-copper-bus-nema-1

It is designated for 42 spaces and 64 circuits. With the 42 spaces, you could have 84 circuits by using space-saver breakers (type QT in Siemens parlance) in every position. Siemens enforces the 64-circuit limit by providing only 22 of the 42 stabs with the notch with allows a space-saver breaker. (Of course this can be circumvented by using non-CTL breakers, but this is non-code compliant unless the panel is very old, made prior to 1965 I believe).
So far, so good.
But then note the language on the far-right of the label: "The installed neutrals limit this panelboard to 64 circuits that require neutral connections. If up to 84 circuits are needed, instal ECNBX kit(s) per schematic."
What on earth does this mean ? You're allowed to use non-CTL breakers to populate up to 84 circuits, if you simply install extra neutral bars ? If so, would this be code-compliant ? Siemens seems to be instructing you to do this if desired; does this override the rule about not using non-CTL breakers on newer panels ?

It is designated for 42 spaces and 64 circuits. With the 42 spaces, you could have 84 circuits by using space-saver breakers (type QT in Siemens parlance) in every position. Siemens enforces the 64-circuit limit by providing only 22 of the 42 stabs with the notch with allows a space-saver breaker. (Of course this can be circumvented by using non-CTL breakers, but this is non-code compliant unless the panel is very old, made prior to 1965 I believe).
So far, so good.
But then note the language on the far-right of the label: "The installed neutrals limit this panelboard to 64 circuits that require neutral connections. If up to 84 circuits are needed, instal ECNBX kit(s) per schematic."
What on earth does this mean ? You're allowed to use non-CTL breakers to populate up to 84 circuits, if you simply install extra neutral bars ? If so, would this be code-compliant ? Siemens seems to be instructing you to do this if desired; does this override the rule about not using non-CTL breakers on newer panels ?