I have a Lift Station with Two, 3phase, 240v, 3hp pumps with 8.9FLA (Nameplate) each. Coming from the meter, there is a 60amp fusible disconnect. Three 6AWG from the disconnect feeds to a Terminal Block in the Control Panel next to the disconnect. From the Terminal Block, Two Sets of 10AWG feed Two 20A Breakers for Branch Ckt. OCP.
Is it ok for the Feeder OCP to be 60amp and 6AWG Feeder Conductor? My calculation says it should be 25amp with 12AWG Feeder Conductor. What am I missing?
Would it be different if it were a breaker?