Curious here. Had nothing to do with anything I'm working on. I came across this.

Utility shall make available temporary electric service for the project. Electrical
Contractor shall provide new 6,000 amp (connected load) 120/208V, 3‐phase, 4‐wire service
for temporary light and power.

Now the calculated load would be different than the connected load they mention and wires, breakers would need to be sized according to the CALCULATED load. Is that correct?
 
If the 6,000A "connected load" is continuous, then the service needs to be 6,000 x 1.25 = 7,500A. You can't buy 7,500A equipment. Even 6,000A is extremely rare.

What on earth could possibly need 6,000A for temporary? What size is the permanent service?

In my world, 6,000A connected load means you added up all the nameplates of the equipment and lights and came up with 6,000A. A 6,000A circuit breaker is not a 6,000A connected load. I get suspicious when the "connected load" is a nice round number like 20A, 400A etc. I'm suspicious that the person giving me the info doesn't mean the same thing as me when we talk about "connected load".
 
We did a large apartment/condo complex (two towers 700+units) we installed 3-4000 amp services for temporary power. Not sure who sold them on that much power but we barely used much of it even with temporary heat.
 
No. Connected load means everything, and ignores that things like heat and A/C won't run simultaneously.
Thanks. So the connected load is NOT the calculated load.

you could have:

80A actual continuous loads
30A actual non continuous loads

But the calculated would be 130A?
 