Connecticut removes smoke detectors from AFCI circuit

Status
Not open for further replies.
Jim W in Tampa said:
wHATS WRONG WITH OUR CLOCK ITS ONLY 7 :57 HERE
According to my forum page, you are correct. You need to go into your control panel and change the time-zone setting.
 
An exception for receptacles that are not readily accessible will be added to an existing amendment to Section 210.8(B), which requires that all 125-volt, single-phase, 15- and 20-ampere receptacles installed within 6 feet of the outside edge of a sink or lavatory to have ground-fault circuit-interrupter protection for personnel.

Section 210.12(B) will be amended by deleting the requirement for AFCI combination type and adding an exception for smoke detectors installed in bedrooms, provided the smoke detectors are not installed on branch circuits supplying other outlets within the dwelling unit bedroom.


So what do you think?? My only problem is that if the outlets are 'not' readily accessible it would be an inconvience to be moving a freezer to just reset a gfci. Just my opinion. :)
 