canote100
Member
- Location
- San Diego, CA
- Occupation
- Electrical Engineer and C10 Contractor
I have a customer that has a Well pump for an avocado farm irrigation system that is being powered by a dedicated 480V corner grounded service (Phase B grounded). He wants to use that service to provide power to a house that he is planning to build for the farm. For that I will need to install a 480V Delta-Wye 120/208V transformer.
Corner grounded systems are not common nowadays and I am not very familiar with them, so I need help on clarifying the following.
1) Will there be any issue with the new Delta- Wye transformer being corner grounded as well since Phase B of the service is already grounded?
2) On the Delta-Wye transformer's nameplate, the Delta diagram shows H1 being the one they identify to be grounded (see image below). Should I connect H1 to Phase B instead of Phase A, or just connect H2 to Phase B and make H2 the grounded corner? is this indifferent to the transformer internally? My understanding is that for corner grounded Delta systems usually phase B is the one grounded.
3) Should I have a dedicated GEC for the secondary of the Delta-Wye transformer, separate from the GEC of the service? (The GEC of the Service and the transformer location would be very close to each other)
Thanks for the clarification here.
Corner grounded systems are not common nowadays and I am not very familiar with them, so I need help on clarifying the following.
1) Will there be any issue with the new Delta- Wye transformer being corner grounded as well since Phase B of the service is already grounded?
2) On the Delta-Wye transformer's nameplate, the Delta diagram shows H1 being the one they identify to be grounded (see image below). Should I connect H1 to Phase B instead of Phase A, or just connect H2 to Phase B and make H2 the grounded corner? is this indifferent to the transformer internally? My understanding is that for corner grounded Delta systems usually phase B is the one grounded.
3) Should I have a dedicated GEC for the secondary of the Delta-Wye transformer, separate from the GEC of the service? (The GEC of the Service and the transformer location would be very close to each other)
Thanks for the clarification here.