I'm an electrical contractor in Texas, I'm also the Master.
I'm hoping this is the appropriate topic to post this here. If not, my apologies to the moderator, I looked over the other topics and this one seemed the most related.
Without naming locations, my office is located 6 hours away from the location in question (Texas is big) and I don't service the area of the location. This job was a one-off because there were no able generator contractors in the area and I was an old friend of the head of maintenance (at the time) for this facility. He begged me to come help him.
In 2022 I installed a stand by generator at a resort. The resort was soon to be completely remodeled and the new generator was the first thing they wanted to get done. I replaced an existing standby generator that was not functioning. All of the existing wiring from the generator to the ATS and from the ATS to the emergency systems power bank was all NEC compliant and didn't need to be replaced or modified. All we did was remove the old generator, set the new one and wire it up the way it was. We shut down the entire facility at 3 am to test the emergency systems. The ATS took over and provided power to the emergency power panels as expected, the elevators ran as normal. We exercised all of the emergency systems that we could except for actually running the fire pumps (but the fire pump system had power). I programmed the generator to exercise itself once a week and verified that it was doing so with the staff maintenance manager for four weeks after the project was complete.
After the generator was set and tested, the facility had the fire alarm contractor onsite the next day to get his system current and compliant. He requested that I run a set of control wires from the ATS to the fire alarm control room. We did this. We installed two runs of CAT6 in EMT from the ATS and terminated them in a 1900 box located in the ceiling of the fire control room, we also left enough CAT6 to run anywhere in the fire control room. The other end is rolled up in the ATS enclosure. It was my understanding that the elevator company was supposed to terminate the signal wires in the ATS & the fire alarm panel to do whatever they are required to do with the elevator in case of a fire or power outage.
Now, two years after and the facillity nearing the completion of the big remodel. Their local electrician is not wanting to connect the wires to the ATS because he really doesn't know where they go. That's understandable because I'm not really sure it is the electricians job to do this. The fire alarm company says it's the elevator company's responsibility and the elevator company says it's my responsibility because I installed the generator.
I don't mind making the terminations nor do I mind traveling that far, if I'm suitably compensated for my time and travel.
My question here is, what would other contractors do in this situation? If I did accept the job, where would I find out what the ATS is supposed to do for the fire control panel and the elevators? It it within the legal coverage of my electrical Masters license in Texas to do such work? Or should the elevator contractor be the one who is responsible?
I'm hoping this is the appropriate topic to post this here. If not, my apologies to the moderator, I looked over the other topics and this one seemed the most related.
Without naming locations, my office is located 6 hours away from the location in question (Texas is big) and I don't service the area of the location. This job was a one-off because there were no able generator contractors in the area and I was an old friend of the head of maintenance (at the time) for this facility. He begged me to come help him.
In 2022 I installed a stand by generator at a resort. The resort was soon to be completely remodeled and the new generator was the first thing they wanted to get done. I replaced an existing standby generator that was not functioning. All of the existing wiring from the generator to the ATS and from the ATS to the emergency systems power bank was all NEC compliant and didn't need to be replaced or modified. All we did was remove the old generator, set the new one and wire it up the way it was. We shut down the entire facility at 3 am to test the emergency systems. The ATS took over and provided power to the emergency power panels as expected, the elevators ran as normal. We exercised all of the emergency systems that we could except for actually running the fire pumps (but the fire pump system had power). I programmed the generator to exercise itself once a week and verified that it was doing so with the staff maintenance manager for four weeks after the project was complete.
After the generator was set and tested, the facility had the fire alarm contractor onsite the next day to get his system current and compliant. He requested that I run a set of control wires from the ATS to the fire alarm control room. We did this. We installed two runs of CAT6 in EMT from the ATS and terminated them in a 1900 box located in the ceiling of the fire control room, we also left enough CAT6 to run anywhere in the fire control room. The other end is rolled up in the ATS enclosure. It was my understanding that the elevator company was supposed to terminate the signal wires in the ATS & the fire alarm panel to do whatever they are required to do with the elevator in case of a fire or power outage.
Now, two years after and the facillity nearing the completion of the big remodel. Their local electrician is not wanting to connect the wires to the ATS because he really doesn't know where they go. That's understandable because I'm not really sure it is the electricians job to do this. The fire alarm company says it's the elevator company's responsibility and the elevator company says it's my responsibility because I installed the generator.
I don't mind making the terminations nor do I mind traveling that far, if I'm suitably compensated for my time and travel.
My question here is, what would other contractors do in this situation? If I did accept the job, where would I find out what the ATS is supposed to do for the fire control panel and the elevators? It it within the legal coverage of my electrical Masters license in Texas to do such work? Or should the elevator contractor be the one who is responsible?