kar108,
Consider a simplistic example of four 12/2 NMB branch circuits running 100' from their overcurrent protective devices (OCPDs) to a 4 gang switch box. Then, another 10' to 4 different loads.
When the EGCs are kept segregated, and a ground fault at one load occurs, the return path to the panel with the OCPDs is through one #12 all the way.
When the EGCs are spliced together, and a ground fault at one load occurs, the return path to the panel with the OCPDs is through one #12 for 10' and through four paralleled #12 for 100'.
The more interconnection points between EGCs, the more likely the reduction of the overall impedance in a fault situation.
Edit syntax - Al