Connecting grounds - separate circuits

Status
Not open for further replies.

kar108

Member
A light switch box has two circuits connected in the box - one for a light, another for switched receptacles. Do the grounds for the separate circuits have to be tied together? I think they do based on 250.148 and 250.96. The contractor says he has never connected these together in the past.
 
Re: Connecting grounds - separate circuits

I don't see how those two articles apply. :confused: I always thought they must be tied together but I can't find anything to tell me this.
 
Re: Connecting grounds - separate circuits

Scott, I think 250.148 is very poorly written, and even a bit confusing. But that is the code section that would require this.

I agree with you about 250.96. I don't see the relevance.

[ October 19, 2005, 05:06 PM: Message edited by: peter d ]
 
Re: Connecting grounds - separate circuits

I agree with Scott I don't see how 250.148 would apply either. It does not say that they must be connected together.
 
Re: Connecting grounds - separate circuits

250.148 Continuity and Attachment of Equipment Grounding Conductors to Boxes
. . .any equipment grounding conductor(s) associated with those circuit conductors shall be spliced or joined. . .
How does it this not apply?

This is exactly the citation I would be given were I not to bond together all the EGCs present in a j-box.

The image I like that conveys the idea inherent in 250.148 is that EGCs form a web or mesh that decreases the impedance. EGCs are, if possible by the wiring layout, not to be kept as spokes on a wheel.

Edit syntax - Al

[ October 19, 2005, 06:29 PM: Message edited by: al hildenbrand ]
 
Re: Connecting grounds - separate circuits

I think it does.

250.148 talks about circuit conductors terminating within the box. That much is clear enough. What it doesn't do is say anything about more than one circuit terminating within the same box. That is where it may get confusing.

But look at the following words from 250.148, and note my bold and all-caps emphasis:
. . . any equipment grounding CONDUCTOR(S) associated with those circuit conductors shall be spliced . . .
OK, so you have four circuit conductors (phase and neutral for circuit #1, phase and neutral for circuit #2). What this tells me is that ALL EGCs associated with any of the four circuit conductors must be spliced. In other words, both EGCs must be spliced.
 
Re: Connecting grounds - separate circuits

OK, so you have four circuit conductors (phase and neutral for circuit #1, phase and neutral for circuit #2). What this tells me is that ALL EGCs associated with any of the four circuit conductors must be spliced. In other words, both EGCs must be spliced.
So if the two circuits, say a 277 volt lighting circuit and a 120 volt receptacle circuit originated from two separate panelboards you would still tie them together?
 
Re: Connecting grounds - separate circuits

Yeah guys like I said 250.148. :eek: I see it now. What helps to clarify is the exception which specifies what is not required to be connected to those grounding conductors. Thanks again NEC word smiths. :roll:
 
Re: Connecting grounds - separate circuits

If I read between the lines the consensus is that the grounds from both circuits should be all tied together.

I don't quite understand the spoke and net analogy - can someone please elaborate.
 
Re: Connecting grounds - separate circuits

Originally posted by infinity:
So if the two circuits, say a 277 volt lighting circuit and a 120 volt receptacle circuit originated from two separate panelboards you would still tie them together?
Yes, there is no exception or distinction made for different voltages and/or different sources.
 
Re: Connecting grounds - separate circuits

Originally posted by infinity:
So if the two circuits, say a 277 volt lighting circuit and a 120 volt receptacle circuit originated from two separate panelboards you would still tie them together?
I would, just as two circuits or voltages sharing a metal-box-and-conduit system would.
 
Re: Connecting grounds - separate circuits

kar108,

Consider a simplistic example of four 12/2 NMB branch circuits running 100' from their overcurrent protective devices (OCPDs) to a 4 gang switch box. Then, another 10' to 4 different loads.

When the EGCs are kept segregated, and a ground fault at one load occurs, the return path to the panel with the OCPDs is through one #12 all the way.

When the EGCs are spliced together, and a ground fault at one load occurs, the return path to the panel with the OCPDs is through one #12 for 10' and through four paralleled #12 for 100'.

The more interconnection points between EGCs, the more likely the reduction of the overall impedance in a fault situation.

Edit syntax - Al

[ October 20, 2005, 12:07 AM: Message edited by: al hildenbrand ]
 
Re: Connecting grounds - separate circuits

Originally posted by infinity: So if the two circuits, say a 277 volt lighting circuit and a 120 volt receptacle circuit originated from two separate panelboards you would still tie them together?
To what the others have responded, I will add this: If there were a fault on a 277 volt load, there would be a path for fault current from the 277 volt source, to the fault point, via the individual 277 V load's EGC to the point at which the EGCs are spliced, and from there back to the 277 V source. That would trip the 277 V breaker.

The fact that there is a connection from the EGC splice point back to the 120 volt source does not alter the path I describe above. Nor does it create a second path for fault current. The 120 V source is not providing current to the fault point, so no fault current will flow back to the 120 V source.

Bottom line: Yes you do splice the EGCs for both systems.
 
Re: Connecting grounds - separate circuits

Originally posted by Charlie B.:
Nor does it create a second path for fault current.
The main bonding jumpers aren't connecting to the same GES in most buildings?
 
Re: Connecting grounds - separate circuits

Sorry, I wasn't clear. I intended that to mean that there will not be a fault current path that involves the 120 volt source. I was addressing infinity's apparent concern about an inadvertent connection of two power sources.

You are right that there will be a second fault path that involves the 120 volt panel's ground bus, GEC, the combined GES, and the 277 volt panel's GEC.
 