Connecting PV to an existing MLO service panel
fandi
Los Angeles
Hello All,
(Under NEC 2014) Would a PV connection (via a PV breaker) to an existing MLO panel considered a supply side connection? (To me it's a load side connection because the PV breaker takes one of the MLO panel's feeder breaker slots)
And if it's not a supply side connection, would this following configuration comply with 705.12(D)(2)(3)(a)?
48A output inverter connects to a 100A MLO panel via a 60A PV breaker.
125% x 48A + 0A <=100A.
Assumptions:
- Manufacturer cutsheet of that MLO panel allows PV system to connect to the panel via a PV breaker.
- the total breakers (PV breaker plus all existing feeder breakers) are no greater than 6.
Also, if it's a load side connection, is there any of the 705.12 section requires the service panel has to have a main breaker in order for the PV system to hook up? I see that NEC 2014 705.22 only requires a disconnect device at the main service panel, not a OCPD. Meaning an external disconnect ahead of the MLO panel would suffice.
Thanks.
jaggedben
Simply, if there is no other disconnecting means between the service point and the PV disconnecting means, then it is not connected on the load side of a service disconnecting means. If it is not load side then it is supply-side.
Meters have nothing to do with it as far as the NEC is concerned.
fandi
Los Angeles
I agree that meters have nothing to do in this case, but I try to find in the Art 100 about the definitions of 'supply side connection' and 'load side connection' and I can't find them. As you can see in my diagram, the PV connection point is still the same spot. So how do we know when will be supply side connection, and when will be load side connection? And just like your interpretation, the Code needs to make it clear in Art 100 that a connection of the load side of the main breaker is considered load side connection.
I think Jaggadben explained it very clearly. Perhaps its a "small" difference having a main breaker in there, but that is the service disconnect and the Pv is on the load side of the service disconnect.
see 705.12(A) and (D). I admit it is not very logically laid out.
ggunn
Austin, TX, USA
Electrical Engineer - Photovoltaic Systems
Yes it is a supply side connection. It is a bit odd that the 120% rule doesnt apply in that situation. I wonder if that was an oversight by the code makers.
The 120% rule cannot apply because there is no OCPD on the panel. There is nothing to base the calculation on because the available current to the bus from the utility side is virtually unlimited.
jaggedben
Article doesn't really need to make that clear when 705.12(A) states things pretty precisely.
I forget if Article 100 defines the service disconnecting means, or just service equipment, but read Article 230 for more in the disconnecting means.
GoldDigger
The 120% rule applies to situations where the current to the bus or conductor from each source is limited and so the bus/conductor is protected. Adding the two current sources would allow a load to draw more current and defeat the protection.
Service conductors are NOT protected, so adding more current from PV will not make things worse. So no 120% rule.
That lack of protection is why service conductors are not allowed to run very far inside.
For what its worth, here is a bit on supply side connections by the Washington State Labor and Industries:
https://www.lni.wa.gov/TradesLicensing/Electrical/files/currents/Elc1410.pdf