Currently working on a job in a residential area adding some electrical sluice gate actuators to control sewage flow in the area. The gate actuators will run on any 3 phase voltage and luckily there is a utility pole with a 3-Can XFMR Bank near where we are planning to install the distribution panel. The 3-Can XFMR Bank appears to be connected to the utility pole secondary mains the same way as in the attached picture below, which from what I have researched I'm guessing the secondary is a 3Ph, 4W High Leg 120/240V Delta service because they are located in a residential area, but I'm definitely not an expert so any input is appreciated. My other question is if this is a 3Ph, 4W High Leg 120/240V Delta service is it a code violation to only connect the 3 240V phases of the secondary delta to the service entry without using the delta connected neutral? Would that change the connection to a Delta Primary - Delta Secondary 240V, 3Ph, 3W connection? I was wonder if I could eliminate the delta connected neutral because it would not connect to any of the gate actuators and the controls engineer said he was connecting all of his I/O to a 240VAC to 120VAC control transformer so the 120V neutral to phase connections would not be used either. Sorry if this is a dumb question, this is the first time I've had to connect a service to a utility pole and I'm a bit lost at the moment. Any Help is appreciated, Thank you.