I am seeking explanation,clarification and guidance on the following Residential Service scenarios:#1 From utility meter enclosure, a 3-wire cable is used,an additional grounding electrode conductor is connected to the grounded conductor. This 3-wire cable enters the service (breaker)panel,there is a "tie-bar" between the neutral (grounded)conducor bar/buss and the grounding bar/buss, and the grounding bar bonding screw is used to bond these to the metal enclosure. yes/no?
scenario#2 From service (breaker)panel mentioned above,a 2-pole breaker is used to feed a "sub-panel" in an attached garage. Does the "tie-bar" between the neutral and grounding bars/buss in the panel in the garage get used ...or is it removed? ...and where is this stated in article 250?
Scenario #3: Meter enclosure is a combination meter/breaker because of long distance to service/breaker panel. Now a 4-conductor cable is used because of Art.250-142(B).In the service/breaker panel,Does the "tie-bar" between the neutral and grounding bars get used or removed? Thanks!
scenario#2 From service (breaker)panel mentioned above,a 2-pole breaker is used to feed a "sub-panel" in an attached garage. Does the "tie-bar" between the neutral and grounding bars/buss in the panel in the garage get used ...or is it removed? ...and where is this stated in article 250?
Scenario #3: Meter enclosure is a combination meter/breaker because of long distance to service/breaker panel. Now a 4-conductor cable is used because of Art.250-142(B).In the service/breaker panel,Does the "tie-bar" between the neutral and grounding bars get used or removed? Thanks!