Background information: I have a 3 phase 480 V motor that was purchased to operate in wye start, delta run configuration. The motor came with a nameplate that only indicates wiring for the delta configuration. There are 12 motor leads in the p-head. I located a proper diagram but this leads to the real question.
The question - While searching the 2008 NEC, especially Article 430 and 430.7 I can find no requirement that calls for a motor label or nameplate to actually include a wiring configuration. Article 430.9 A (Terminals) almost gets there but it seems like a short-cutting manufacturer could just label the terminals T1, T2 etc and meet the "letter" of the code. Does anyone know of a code requirment that requires a labeled wiring configuration for motors (or have I misinterpreted 430.9 A)?
Please forgive me if I have overlooked something obvious. I have worked with the code for years but learn something new weekly.
The question - While searching the 2008 NEC, especially Article 430 and 430.7 I can find no requirement that calls for a motor label or nameplate to actually include a wiring configuration. Article 430.9 A (Terminals) almost gets there but it seems like a short-cutting manufacturer could just label the terminals T1, T2 etc and meet the "letter" of the code. Does anyone know of a code requirment that requires a labeled wiring configuration for motors (or have I misinterpreted 430.9 A)?