I need to Connect An Aluminum Cable 185 mm2 to Terminal Block PA66 Insulated and Tinned Coper Plated Current Bar. Cause of Two Different type of Material to Be Connected - Copper & Aluminum.

Pls advise.

Regards,
skhamis
 

charlie tuna

Senior Member
Location
Florida
the terminal block should be rated for aluminum.
it should be cleaned.
the conductor should be stripped without damaging the strands.
use a rated inhibitor like kno-lox to coat the aluminum exposed surfaces.
apply proper torque.
wiggle conductor --- re-torque.
finished.......................
 