K1GMB
Member
- Location
- North Chesterfield, Virginia 23236
- Occupation
- Telecommunications Engineer (Master Electrician)
I am installing four (4) individual hubble 20-amp surge arrestor outlets in a non-metallic outlet box. Each hubble surge arrestor outlet will be dedicated to a single Square D QO CAFI circuit breaker. There are individual runs of 12-2 from the electrical sub-panel to each surge arrestor. At the sub-panel, all grounds are connected to a separate grounding buss bar, connected back to the main electrical panel, AND a connection to a locally 8' driven copper electrode. Because of the CAFI, there are separate neutrals and hots for each surge arrestor receptacle. My question is, do I need to tie all grounding conductors together in the non-metallic outlet box? Electrically the #12 grounding conductor of each surge arrestor receptacle is a home run back to the ground buss bar in the sub-panel. Electrically there is a dedicated earth ground on each circuit. In researching Article #250, (2020 NEC edition), I found section 250.140 (D) that seems to address my question. I really don't want to have to tie up space in this quad outlet box unless I absolutely have to. Thanks!!!!!