There is an interesting note attached to table 250.122 that says:
Note: Where necessary to comply with 250.4(A)(5) or (B)(4), the equipment grounding conductor shall be sized larger than given in this table.
Cooper has an interesting paper on protecting the EGC here: http://www.cooperindustries.com/con...ductor_Protection_Wire_Cable_Protection_1.pdf
Outside of upsizing the EGC when the associated current carrying conductors are upsized for some other reason has anyone found a reason to upsize the EGC?
Note: Where necessary to comply with 250.4(A)(5) or (B)(4), the equipment grounding conductor shall be sized larger than given in this table.
Outside of upsizing the EGC when the associated current carrying conductors are upsized for some other reason has anyone found a reason to upsize the EGC?