Re: 501.15(E)(1): "... Multiconductor .. cables with a gas/vaportight continuous sheath capable of transmitting gases or vapors through the cable core that are installed in Division 2 location shall be sealed with a listed fitting after the jacket and any other coverings have been removed ... ".
We have a situation where we have a 250MCM 3/C cable capable of transmitting gases/vapors through the core fed from a non-hazardous source into a Class 1 Div 2 Group D area supplying a switchrack with explosion-proof gear. So necessarily we need seals on this cable within 10' +/- of the boundary, and within 18" of the main breaker.
Now the electricians have already pulled this cable in the conduit and had planned on using the normal method of treating it as a single conductor and filling with CHICO around the outside jacket... only for our city inspector to stop them in their tracks. I agree with the inspector on this after reviewing the code.
My question is 1) can we place the boundary seal in the 10 feet of the non-classified zone and thus exempt ourselves from the requirements of 501.15(E)(1) since it's technically not in a Class 1 Div 2 zone? Ok being a bit cheeky here.
My real question is 2) What is the best way for them to proceed? Surely they don't pull the cable back out from the nearest LB, cut off the jacket at juuust the right distance, then pull it back through conduit without the protective outer layer? Are they able to cut off the jacket and remove what they need through the small hole? How would this be approached normally? Easiest to just buy a pre-sealed termination box at this point?
First time dealing with this requirement.
Thanks,
We have a situation where we have a 250MCM 3/C cable capable of transmitting gases/vapors through the core fed from a non-hazardous source into a Class 1 Div 2 Group D area supplying a switchrack with explosion-proof gear. So necessarily we need seals on this cable within 10' +/- of the boundary, and within 18" of the main breaker.
Now the electricians have already pulled this cable in the conduit and had planned on using the normal method of treating it as a single conductor and filling with CHICO around the outside jacket... only for our city inspector to stop them in their tracks. I agree with the inspector on this after reviewing the code.
My question is 1) can we place the boundary seal in the 10 feet of the non-classified zone and thus exempt ourselves from the requirements of 501.15(E)(1) since it's technically not in a Class 1 Div 2 zone? Ok being a bit cheeky here.
My real question is 2) What is the best way for them to proceed? Surely they don't pull the cable back out from the nearest LB, cut off the jacket at juuust the right distance, then pull it back through conduit without the protective outer layer? Are they able to cut off the jacket and remove what they need through the small hole? How would this be approached normally? Easiest to just buy a pre-sealed termination box at this point?
First time dealing with this requirement.
Thanks,