I happened to go over some electrical questions from the Craftsman Electrician?s Exam Preparation Guide for the 2008 NEC.
Run into this question below ?
A department store is illuminated with 215 fluorescent lighting fixtures and connected to a 120-volt supply. Each lighting unit draws 2.2 amperes. How many 20-ampere branch circuits are necessary to feed these fixtures if each branch circuit must not exceed 80% of the branch circuit?
The solution given: 215 fixtures x 2.2 = 473 amp, total load. A 20- amp branch circuit load to 80% of its capacity = 20 x.80 =16 amperes. 477 amperes (total load) / 16 = 29.56 or 30 circuits.
The answer (30 circuits) does not seem correct,
Without the 80% de-rating): I total = 215 units x 2.2 amps = 473A/20 = 23.65 (24 circuits)
This was my answer - with the 80% de-rating: this seems more seems logical: 473 x 80% = 378.4A/20 = 18.92 (19 circuits).
This question is a bit confusing, because, de-rating means to decrease this method seems to add.
This question does not sound logical ? 30 different circuits for a 20 amp branch circuits for a light that only consumes (2.2amps x 120V) 264 watts?
Not as per reference rule 220.18(B), and 210.11, Also, that means 30-2 pole circuit breakers will be needed and that?s equivalent to 60 breaker, which means a least two panels ? due to the 42 max per panel as per rule- 408.54 Maximum Number of Overcurrent Devices. A panelboard shall be provided with physical means to prevent the installation of more overcurrent devices than that number for which the panelboard was designed, rated, and listed.
For the purposes of this section, a 2-pole circuit breaker or fusible switch shall be considered two overcurrent devices; a 3-pole circuit breaker or fusible switch shall be considered three overcurrent devices.
To de-rate means to decrease ? not increase. As per rule- 210.23 (A) (1) Cord-and-Plug-Connected Equipment Not Fastened in Place. The rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.
What a big difference 30 circuits (11 more), which seems to spell out an overload.
What is the ampacity needed to size the conductor for each branch circuit? Is it 2.2 amps for each branch circuit ? is it a minimum of 18 AWG as per 600.31 (B)?
Can someone please explain this better?
Run into this question below ?
A department store is illuminated with 215 fluorescent lighting fixtures and connected to a 120-volt supply. Each lighting unit draws 2.2 amperes. How many 20-ampere branch circuits are necessary to feed these fixtures if each branch circuit must not exceed 80% of the branch circuit?
The solution given: 215 fixtures x 2.2 = 473 amp, total load. A 20- amp branch circuit load to 80% of its capacity = 20 x.80 =16 amperes. 477 amperes (total load) / 16 = 29.56 or 30 circuits.
The answer (30 circuits) does not seem correct,
Without the 80% de-rating): I total = 215 units x 2.2 amps = 473A/20 = 23.65 (24 circuits)
This was my answer - with the 80% de-rating: this seems more seems logical: 473 x 80% = 378.4A/20 = 18.92 (19 circuits).
This question is a bit confusing, because, de-rating means to decrease this method seems to add.
This question does not sound logical ? 30 different circuits for a 20 amp branch circuits for a light that only consumes (2.2amps x 120V) 264 watts?
Not as per reference rule 220.18(B), and 210.11, Also, that means 30-2 pole circuit breakers will be needed and that?s equivalent to 60 breaker, which means a least two panels ? due to the 42 max per panel as per rule- 408.54 Maximum Number of Overcurrent Devices. A panelboard shall be provided with physical means to prevent the installation of more overcurrent devices than that number for which the panelboard was designed, rated, and listed.
For the purposes of this section, a 2-pole circuit breaker or fusible switch shall be considered two overcurrent devices; a 3-pole circuit breaker or fusible switch shall be considered three overcurrent devices.
To de-rate means to decrease ? not increase. As per rule- 210.23 (A) (1) Cord-and-Plug-Connected Equipment Not Fastened in Place. The rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating.
What a big difference 30 circuits (11 more), which seems to spell out an overload.
What is the ampacity needed to size the conductor for each branch circuit? Is it 2.2 amps for each branch circuit ? is it a minimum of 18 AWG as per 600.31 (B)?
Can someone please explain this better?