DanaeV
Member
- Location
- Green Bay, WI 54303, USA
- Occupation
- Automation & Instrumentation Controls Specialist
Hello. I am troubleshooting one of our HP Electro-Magnetic Vibrating Feeders. I have checked all fuses, voltages, terminations, etc., I stand by it and have the operator start the feeder, I watch it start for approximately 3 seconds and then it'll kick out. Due to a previous issue that I located (wire nut wore thru caused an arc in the enclosure on the feeder itself) and the age of the system, my first thought was that the contacts are worn/shot. I happened to have one on hand and swapped it out. Once again had the operator start it and again it ran for 3 seconds and kicked back out. I'm looking to see if there is anyone out here that may be able to point me in a direction of what to check next. In this system, there are the following components: Control Transformer, Starter(Contactor), Diode with Heatsink (SCR), 2 Line Fuses, a Transformer Fuse and a control board that appears and test good. The Feeder is a Jeffrey Dresser (No longer in business, only company I've been able to find that still deals with this mfg. is TerraSource), Model M050. Thank you in advance for any help/ideas you may have!