When you read a contactor and it says 40amp resistive does that mean continuous? And what about a load with harmonics, like a lot of ballasts, what would that do to the rating?

I have seen contactors with 50a resistive, 40 a FLA ratings. Less inductive current allowed.

I don't think that you need to limit a continuous load to 80% of the contactor rating, though I would limit an inductive load to 80% of the resistive rating.
 