Yes NEMA size - the contactor is to start/stop a 1ph 208 volt rotary phase converter which is listed @ 30kw and 250 amps- I'm guessing size 4 but I don't have the literature available at this time.
 
I guess it was pointed out to me the other week that rotary phase converters don't require starters or overloads units of any sort. Just an ordinary OCPD.
 
mdshunk said:
I guess it was pointed out to me the other week that rotary phase converters don't require starters or overloads units of any sort. Just an ordinary OCPD.

For clarification, I know that. The contactor controlled by a selector switch or other control means affords the opportunity to control the RPC from a remote location without civilians going into the Dist Panel and flipping brkrs.
 