The project I am on they put a contactor in between the main switch for a 480-volt Transformer so they could control 120 208 panel under a load
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
The project I am on they put a contactor in between the main switch for a 480-volt Transformer so they could control 120 208 panel under a load
Done all the time. At least 90% of Home Depot’s does this to control display panels. It is cheaper to control the primary of the transformer because the contactor is roughly 50% smaller.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Done all the time. At least 90% of Home Depot’s does this to control display panels. It is cheaper to control the primary of the transformer because the contactor is roughly 50% smaller.
Yep, pretty common. You also save on the xformer losses while it's off. Just gotta be sure the contactor is rated for the inductive inrush.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Yep, pretty common. You also save on the xformer losses while it's off. Just gotta be sure the contactor is rated for the inductive inrush.
And that someone is willing to live with the contactor hum (added to the transformer hum) when it is energized.
If not, using a latching contactor is the way around that.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
And that someone is willing to live with the contactor hum (added to the transformer hum) when it is energized.
If not, using a latching contactor is the way around that.
Maybe with newer "Smart" contactors you can select a tune rather than a hum :) True ??:
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Maybe with newer "Smart" contactors you can select a tune rather than a hum :) True ??:
If not, I'd be willing to bet someone is now working on making that upon your suggestion... :unsure:

One of our engineers made a demo unit that uses the sounds made by the stepper motors to play the "Darth Vader" theme from Star Wars. He got the idea from this video.

Our boss was not amused because he understood how much time that would have taken. But the rest of us were impressed.
 