Contactors in JB

Status
Not open for further replies.

LYLE2231

Member
Good Morning Friends, I ran across an installation during an inspection where the EC had installed -3- 2pole definite purpose relays for lighting control. My question is "Does this require a testing labs listing" Because this is a "field assembled" part does it even require a listing if the box is listed and the relays are listed. Thanks ! Lyle :cool:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
There is nothing requiring this to be listed as an assembly.

Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I believe that there would only be listing requirement would be if these were used for emergency lighting circuits.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Good Morning Friends, I ran across an installation during an inspection where the EC had installed -3- 2pole definite purpose relays for lighting control. My question is "Does this require a testing labs listing" Because this is a "field assembled" part does it even require a listing if the box is listed and the relays are listed. Thanks ! Lyle :cool:

It certainly seems to be an industrial control panel as defined by article 409. Does the code require a listing for industrial control panels?