leftcoastsparky
Question.....200 amp service, #6 to ground and #4 to main water pipe?
#6 to ground rods and #4 to water pipes... That is correct
Dennis.....
what if ???
1. It's a commercial 200 amp service with 3/0 cu conductors ?
2. I install my grounding electrode conductor to my ground rod and from there to my water pipe ?
If this is a new building you will be required to install a concrete encased electrode per 250.52(A)3
Unless I am mistaken, I dont believe that a CEE is ever "required" to be installed. It is my understanding that you are required to connect to one if it is present.
Pete
Tom is correct if using 2008-2011 Art 250.50 where none of the electrodes are present. In new construction it would be very unusual if electrodes are present (I.e. existing agri-well) before beginning a project. (Remodel extension not included.)
I agree that where no electrodes are present something must be installed but I find no requirement that a CEE is REQUIRED to be installed.
250.50 Grounding Electrode System.
Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.
Given this verbiage I do not see where a CEE is required to be installed.
Pete
The timeline of existence is debatable... but for new construction it all usually exists on paper first, and that eliminates the timeline debate IMOYou're right Pete.
But before that foundation gets poured, I will guarantee that any AHJ on the adopted NEC will make sure the foundation UFER is connected because the rebar is part of the a structure requirement and is present, as the CEE per 250.52(A)(3) before the concrete pour. Unless one of the other electrodes are installed and bonded to the permanent panel disconnect before the foundation is poured would be difficult. The way the 250.50 is stated can corner the EC just by interpretation in hooking up a GEC to the rebar. Depends on what the AHJ is thinking on a cya basis.
You're right Pete.
trying..![]()
The timeline of existence is debatable... but for new construction it all usually exists on paper first, and that eliminates the timeline debate IMO![]()
Pete
Your reply makes me uncertain how you took my post... but FWIW I am in agreement with you.The time line begins upon plan check approval for the building permit. NEC 250.50 or 250.52(A)(3) encased #4 is base on a CEE. IRC R403.1.3.1 (stemwalls) and R403.1.3.2 (slabs) mandate #4 CEE to be installed prior to concrete pour.
I doubt most local AHJ's have not applied adopted rebar requirements to avoid the heavy court liabilities that can overrule in a civil court. First up, I would not gamble by constructing a dwelling without rebar and secondly, would you buy a home that was constructed without rebar in a foundation? Timeline for installing a CEE starts with the foundation, unless you are constructing a pole house under a permitted project.
Furthermore, I believe the 250.50 Exception implies that only CEE's of existing buildings and structures are exempt. My interpretation of existing building or structure means after CoO has been issued, or project is deemed completed where occupancy is not at issue.