Continuity between phase conductors, neutral, and ground

Jacobbaker522

Member
Location
Idaho
Occupation
Electrician
Hey everyone,

I had a client contact me after she woke up in the middle of the night to a loud pop. When she got up the next morning all of her individual breakers in a main lug panel had tripped. She reset all of the breakers and everything held. She then called me to come take a look. When I arrived I tightened all of the connection on each breaker as well as the incoming feeders into her panel. This unit is a condo building and her service is 120/208. I grabbed my multimeter to check voltage and continuity. All voltage read correct, but I checked continuity I was getting a very loud ring between both phase conductors, neutral, and both phase conductors to ground. I was also reading over 500 ohms when checking between phases. The panel was energized while I was doing this test so I am assuming that is why I had such high resistance between everything. My question is why would I have continuity with a high pitch ring on my fluke meter between my phase conductor and grounding conductor. Wouldn't this indicate a short?

Thanks for your help.
 

Jacobbaker522

Member
Location
Idaho
Occupation
Electrician
Why are you checking continuity on live circuits?
Meters have been known to explode when this is done.
I did not have the ability to turn off the main breaker and I wanted to make sure the I did not have any shorts between conductors. Do you think because I performed this test while it was live I may have fried my tester and that is why I am getting the ringing between my hot and ground?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Your meter's loud ring is its way of warning you that you are measuring a live circuit on the wrong setting and should stop. It does not indicate a short. And you should ignore any ohm readings in that situation.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Are the individual breakers all AFCIs? I can't think of much that would plausibly trip all the branch breakers in a panel if they weren't AFCIs. Never seen that sort of thing happen,.
 

Jacobbaker522

Member
Location
Idaho
Occupation
Electrician
Are the individual breakers all AFCIs? I can't think of much that would plausibly trip all the branch breakers in a panel if they weren't AFCIs. Never seen that sort of thing happen,.
I haven't hear of it happening before either, there are no AFCI's. My first thought was there was a surge from the utility, but as far as I am aware it only occurred in this one unit. Everything is operating correctly and no equipment was damaged, but I was wondering if anyone had any thoughts on the issue for why each of the branch circuit breakers tripped.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Do you have any idea for why each of the individual branch circuit breakers would have tripped?
Did you witness them tripped? If not, the customer might have been mistaken. They could have turned them all off, then back on thinking that would help. I've had customers tell me half there power was out when it was only one circuit.
 