Charlie Bob
Senior Member
- Location
- West Tennessee
I did a hot tub installation yesterday. Went back today to finish thing up.
I got my fluke T5 and check for continuity at Hot Tub GFCI disconnect.
I checked the feeder first (Line side, from panel box.), everuthing OK.
I checked the supply side then, and had:
L1-L2 OK
L1-N , L1-G OK
L2-N 35 Ohms. (Meter beeped)
First thing i thought was that we nicked them wires when we pulled them. I used EMT against a wall from HT disc. and then went to LFNC 3/4" to control box in Tub.
I disconnected the supply line at the Hot Tub control box, and everything was just perfect.
Hooked the wires back up, and again 35 Ohms from L2-N.
I Turned power on and everything is OK, breaker held, and GFCI never tripped.
I can guarantee everything i did from Panel box to hot tub is OK, and double checked.
What do you think there's in the Hot Tub that will make my meter to read 35 Ohms from L2 to N,?
I did the required convertion from 110v to 240v specified by Manufacturer.(which consisted of a little switch being swapped from on to off)
I got my fluke T5 and check for continuity at Hot Tub GFCI disconnect.
I checked the feeder first (Line side, from panel box.), everuthing OK.
I checked the supply side then, and had:
L1-L2 OK
L1-N , L1-G OK
L2-N 35 Ohms. (Meter beeped)
First thing i thought was that we nicked them wires when we pulled them. I used EMT against a wall from HT disc. and then went to LFNC 3/4" to control box in Tub.
I disconnected the supply line at the Hot Tub control box, and everything was just perfect.
Hooked the wires back up, and again 35 Ohms from L2-N.
I Turned power on and everything is OK, breaker held, and GFCI never tripped.
I can guarantee everything i did from Panel box to hot tub is OK, and double checked.
What do you think there's in the Hot Tub that will make my meter to read 35 Ohms from L2 to N,?
I did the required convertion from 110v to 240v specified by Manufacturer.(which consisted of a little switch being swapped from on to off)