Continuity testing

Status
Not open for further replies.

Nobleone

New User
Location
PA
Occupation
Electrician
when testing continuity between neutral and ground; should I have continuity on the load side (lights) side, with the homerun wires disconnected. Or is there a pinched neutral etc.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Neutrals and grounds are all connected together back at the panel so there should always be continuity. You would need to disconnect both ends and then see if there is a connection
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
when testing continuity between neutral and ground; should I have continuity on the load side (lights) side, with the homerun wires disconnected. Or is there a pinched neutral etc.
Welcome to the forum.

If a neutral is disconnected at the source end, it should be as isolated from ground as a hot conductor.
 