Strombea
Senior Member
- Location
- Prescott, Arizona, USA
We wired a detached garage 200amps under ground from 400a panel, with sub panel inside garage, with a disconnect on the exterior. I ran uffer to the disconnect and a Polaris connecter to connect the uffer to the aluminum SER sub feed wire ground conductor(SER wire feeds panel in garage that supplies all circuits for that building). Inspector is saying uffer has to be continuous all the way to the sub panel and that my connection has to be irreversible in the disconnect. But I'm arguing that the "continuous" is only to service or feeder entrance of which would be the disco. So the Question is:
Where is the NEC defining the ends of the "continuous" conductor? Electrode at one end obviously, other end??? Service entrance? Distribution panel? Etc.
i told him that if I wanted to I could put a listed approved lug kit in disco to attach both wires as in a normal situation with ground bar holding uffer and gas bond and all other sub panels and those sub panels don't have to be continuous.
Please help
Where is the NEC defining the ends of the "continuous" conductor? Electrode at one end obviously, other end??? Service entrance? Distribution panel? Etc.
i told him that if I wanted to I could put a listed approved lug kit in disco to attach both wires as in a normal situation with ground bar holding uffer and gas bond and all other sub panels and those sub panels don't have to be continuous.
Please help