I am doing a load calc for a 4160V feeder serving a transformer tap. The feeder is tapped so that there are now (4) 4160-480/277V, 1500 KVA each transformers off the same breaker upstream (I am adding one to make 4). I'm worried about NEC 215(3)(B)(1). We only have 500 KMIL conductors - the 500 KCMIL comes off the upstream breaker, and is then tapped at 500KCMIL to all (4) transformers. The code says the feeder must be sized for nameplate ratings of transformers being supplied. No way I can do this, as the combined rating of all transformers would require a massive feeder. I'm hoping I can use NEC 215(3)(B)(3), since we are an engineering firm and the facility has maintenance personnel. I'm not sure if they have formal training though, but they work with HV on their site all the time.
The reason I am not concerned load wise, is because I have metering data on worst case. The existing load only uses 147A (worse case) total of all transformers existing. I am rating my underground conductors at 300A per NEC Table 310.60(c)(77), so we should be fine right?
My next question is concerning continuous and non-continuous. I don't see anywhere in the HV feeder section or overcurrent section where 125% continuous must be used. Therefore, I will take my new load as is. However, I will use 125% on the metering load per NEC 220.87. Is this correct?