I have a 3 phase 208 Volt 20hp air compressor.
Name plate FLA 60 amps.
430.250 FLA 59.4 amps
It is replacing a smaller 3 phase compressor supplied by #6thhn.
The note below table 430.22(E) reads: "Any motor application shall be considered as continuous duty unless the nature of the apparatus it drives is such that the motor will not operate continuously with load under any condition of use."
I'd say this motor will will not operate continuously under any condition of use.
Can the existing circuit be used with this compressor considering the note quoted, or must it be upsized to #4?