Continuous GEC

Merry Christmas
Status
Not open for further replies.

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
In relation to 250.64(C) , where the GEC is to be unspliced except by irreversible means, (i.e. crimp splice, exothermic welding, etc.), what would be a clear example of (2) busbars connected together? That would not include splicing from multiple service disconnecting means enclosure ground bus to ground bus would it? Thanks for opinions and interpretations.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The only thing I can think of is the large copper bus section that is installed on commercial job for the grounding electrodes conductor's.


qid267.jpg
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Although it is not the GEC the EGC bus at the bottom of the photo is bolted together.
Tap Section 001.jpg
 

Greentagger

Senior Member
Location
Texas
Occupation
Master Electrician, Electrical Inspector
Thanks guys, that’s kinda what I was visualizing to. Maybe cept the photo of the IBT.
 